- Location
- Wisconsin
- Occupation
- PE (Retired) - Power Systems
An isolation transformer would typically only mitigate issues caused by the load side of the transformer, stray voltage/current caused by the utility could still be a concern
Removing this 'grounded conductor' bonding creates an isolation transformer. The 'grounding conductors' would still connected.Could one use 250.6(B) to "Stop Objectionable Current" by removing the primary to secondary bonding?
Removing this 'grounded conductor' bonding creates an isolation transformer. The 'grounding conductors' would still connected.
That's kind of what I'm thinking. This isolated grounding would be local to the dock area, and the separation from the primary grounded conductor would not be a path for remote, "stray" voltage to return to the utility...., could you ground the derived secondary to a local grounding electrode that was _isolated_ from the primary EGC?
-Jon
Typically the utility system is an MGN bonded to the same dirt as the isolated grounding electrode.Does NEC require the primary EGC be connected to the secondary GEC? Or is this simply common practice because common transformers have a single chassis and a single grounding lug?
If you had a transformer with a non-metallic enclosure, with grounding of the core somehow isolated to only one or the other side, could you ground the derived secondary to a local grounding electrode that was _isolated_ from the primary EGC?
-Jon
Typically the utility system is an MGN bonded to the same dirt as the isolated grounding electrode.
Golddigger's Neutral Isolator automatically closes during a fault.You would need a transformer that somehow isolates primary and secondary terminals, and provides a separate 'ground fault current path' for each.
Does NEC require the primary EGC be connected to the secondary GEC? Or is this simply common practice because common transformers have a single chassis and a single grounding lug?
If you had a transformer with a non-metallic enclosure, with grounding of the core somehow isolated to only one or the other side, could you ground the derived secondary to a local grounding electrode that was _isolated_ from the primary EGC?
-Jon