D domnic Senior Member Occupation Electrical Contractor Dec 7, 2017 #1 when to use 100 mA and 30mA gfi on boat dock?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 7, 2017 #2 do you know which Code cycle is in play ?
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Dec 7, 2017 #3 To be specific, the limit was 100 ma in the 2014 NEC. It was reduced to 30ma in the 2017 NEC. In Washington State, the limit will remain 100 ma for feeders only until next year. Branch circuits are still limited to 30 ma.
D domnic Senior Member Occupation Electrical Contractor Dec 7, 2017 #4 boat dock augie47 said: do you know which Code cycle is in play ? Click to expand... 2014 nec