boiler thermal cutout

Status
Not open for further replies.
bill@usps06492 said:
What NEC art will I find it required to install a thermal cutout in the branch circuit for an oil or gas boiler?

None.

In MA and I bet CT as well it is in the 'oil burner' section of the fire codes.
 
nyerinfl said:
I could be wrong, but I don't think they do. 424.73 and 424.83 cover boiler thermals, but not for gas.

Thats a good point, I have only seen a written requirement for oil burners.

In some areas the fire department has insisted on them for Gas as well and for me it has been more efficient to comply then fight it. You need to know when to pick your battles.
 
I did look at both art 424.73 & 424.883 but it was my impression that these articles where referring to the limiting of temp of liquid from the boiler, and overpressurized tanks. I should have been more clear in my description, this device looks like a sprinkler head, it mounts onto 4" square, and is adjusted by turning the knob on a threaded post to adjust it's thermal cut out minimum threshold. It has 2 terminals that the line and load side of the circuit is tied into. These units are sometimes referred to as a "fire eye", and their sole purpose is to cut out the power to the boiler incase of a fire onthe boiler or in the basement.
Bill.... (thanks for the help.....)
 
Last edited:
That would be the wrong discription of a fire eye the fire eye is used to to tell if the pilot is lite and flame is on (the correct term is flame sensor). I believe what you are describing it is called a thermal interlock switch. In Mn that is governed by the DLI, in residencial it is a fire code and would be required by boiler size..
 
Bill I knew exactly what you meant, here we call it the 'Firematic' and the requirement for it is not in the NEC.

In MA the requirement is in the oil burner code.


527 CMR: BOARD OF FIRE PREVENTION REGULATIONS

527 CMR 4.00: OIL BURNING EQUIPMENT

4.04:(4)(e) An electrical thermal switch fused to break the ungrounded conductor in the main circuit at 165?F, shall be installed in the main power line within six feet over the top of the burner-boiler or burner-furnace. If the ceiling above the burner-boiler or burner-furnace exceeds 12 feet in height, an additional thermal switch shall be installed on the ceiling and connected in series with the lower switch.
 
Ahhhh....the phantom Firomatic code strikes again. ;) This has to be one of the most misused and misunderstood devices in New England. It doesn't help that most inspectors don't understand that this device is for OIL BURNERS ONLY! Yet they insist they get installed over all furnaces and boilers regardless of fuel type. But as Bob said, this is a battle not worth fighting most times...unless you have a brand new 50 unit condo development to deal with.

But what do I know? I'm sure that firomatic will prevent a home being turned into a pile of matchsticks from a gas burner explosion. :rolleyes: ;)
 