Good day, I am having trouble finding how many labor units it takes to install a bolt-on breaker. I don't see a section for it in the NECA MLU. Does anyone have experience with this issue?
 
What size breaker ?


Miniature breakers I use

1/P - 0.2 - 0.3
2/P : 0.3 - 0.5
3/P : 0.4 - 0.6

Industrial type breakers can be an hour or several

Sent from my iPhone using Tapatalk
 
Last edited:
We are talking 20A 1P up to 60A 3P. I would be more inline with your numbers but I have a contractor using the wrong table in the MLU and trying to say "it more closely aligns with this table", only thing is it's the "Terminations" table. Trying to find something more concrete to argue with.
 