Does the NEC say you have to use bolt in breakers for commercial and industrial panels? TY.
GG said:Does the NEC say you have to use bolt in breakers for commercial and industrial panels? TY.
GG said:Does the NEC say you have to use bolt in breakers for commercial and industrial panels? TY.
Jim W in Tampa said:"Also if you want to use the breakers as switches bolt on breakers are a typical answer"
Exsplain that to me Bob.
iwire said:If you plan to use the breakers as daily light switches for fluorescent or HID lights which is common in some commercial occupancies the breakers must be rated 'SWD' or 'HID' I believe all bolt on breakers have the SWD / HID rating, I do not belive many (if any) plug in breakers have the SWD rating. 240.83(D)
When I see plug in breakers used as switches they are usually falling off the bus and held loosely in place by the panel cover.
cpal said:Bobs mention ao avialble fault current levels is critical in the application of OCPD and also ahs a flow over impact on the impletation of NFPA 70 E.
Where high fault levels are present Plug in breakers may be convenient for maintenance proceedures untill there is a flash over and someone is injured. This would be a good discussion.
Charlie
I agree,but just why do they cost more.I also check all the screws on pre breakered panel.infinity said:I prefer bolt-on breakers and would use them on all of my installations if they weren't a lot more expensive not just the commercial applications.
dlhoule said:I woulld agree with you on this, except in most cases the supply feeding the panel can be shut off. Granted in many instances people do not want to do this; but unless you can show me how it might be more dangerous to kill the power to the panel, I'll continue to disconnect the power to the panel before changing a breaker.
My larger concern is appling the proper breaker with the available fault current, besides 70E is structured to discourage any maintenance on energized systems.
Charlie
cpal said:besides 70E is structured to discourage any maintenance on energized systems.
iwire said:I agree, maintenance (outside of trouble shooting) is really not allowed to be done live with or without PPE.
The only way OSHA would let you change a breaker live is if shutting it down would present a greater hazard.
If there is an accident it will be tough to argue with smoke lingering in the air that not shutting down was the safer choice to make.
JMO