Wow, there are alot of under educated bolts out there....(sorry, could not resist)amptech said:No such animal as grade 3 or grade 4 bolts as far as I know.
iwire said:Who is to say that a 10/32" bolt in a 1/4" hole is adequate?
Without having it tested after the fact IMO an inspector could ask for either full size hardware or a paper from the manufacturer.
Clamping pressure between the lug and other material is directly effected by the hardware size and strength.
If a 10/32 is 'OK' in a 1/4" hole is it also OK in a 1/2" hole?
If I was an inspector I might say 'not approved'.
BTW I practice what I preach
Four grade 3 - 1/2" bolts in each lug hole.
![]()
Why, whichever size fits your bolts, of course!jim dungar said:I know that you can purchase lugs with holes ranging from 0" (drill your own) up to at least 1/2" all for the same wire size.
If any one lug can have so many different size holes, which size is correct?
Better yet, how do you get four bolts in each hole? :-?amptech said:"Four grade 3 - 1/2" bolts in each lug hole. "
Question: Where do you buy a "grade 3 " bolt?
jrannis said:Would it be ok to use that last hole even though its hangin over the busbar?![]()
jim dungar said:According to an application bulletin from FCI/Burndy they suggest but do not require sizing bolts at about 75A per 1/8", so:
amptech said:"Four grade 3 - 1/2" bolts in each lug hole. "
Question: Where do you buy a "grade 3 " bolt?
iwire said:That is something I wondered as well, my gut reaction is no, and I did not have to.
TOOL_5150 said:You really honestly do not believe there is enough surface contact on that lug for the [potential] last EGC to be able to clear a short?
TOOL_5150 said:You really honestly do not believe there is enough surface contact on that lug for the [potential] last EGC to be able to clear a short? Would an engineer have to determine this situation?
I would be interested to know a for-sure yes/no about that. One can never know too much.![]()
~Matt
With all the meat in those lugs, I wouldn't have hesitated in the least.iwire said:That is something I wondered as well, my gut reaction is no, and I did not have to.jrannis said:Would it be ok to use that last hole even though its hangin over the busbar?![]()
LarryFine said:With all the meat in those lugs, I wouldn't have hesitated in the least.
That, and looking at the other three outside lug holes, including the large conductor closest to the cabinet. Why doesn't it need to be nearer a bolt?iwire said:And what would you base that decision on?
Your gut feeling?
I ain't 'fraid of no ghost! No, the body of that lug is way too thick for its melting to bother me.If the equipment was to melt down for any reason that decision could come back to haunt you.
LarryFine said:That, and looking at the other three outside lug holes, including the large conductor closest to the cabinet. Why doesn't it need to be nearer a bolt?
I ain't 'fraid of no ghost! No, the body of that lug is way too thick for its melting to bother me.
benaround said:Does that lug ground anything more than the enclosure ? It seems all the
grounding is taken care for in the lug itself, except for the enclosure.
iwire said:I honestly do not know and not knowing should make us go on the side of caution.
In most instances I am sure it would be fine, on the other hand that lug can handle four 600 copper conductors and the fault current that lug could be expected to handle could easily be many hundreds of thousands of amps.
How do you know that the way you have joined these two lugs is adequate? What kind of guess did you make that this would work? Do you have the incoming and outgoing EGCs in any particular order? Did you use an oxide inhibitor?iwire said:Well as long as your comfortable with a WAG on something like that because thats all it is.
No science, no research just a WAG.
Whats the worst that can happen other then it failing under a high ground fault condition. :grin: