I have a greenhouse where I will be putting a gutter in between the 480v panel and the grow control Panel. I usually would do this using a 3" rigid coupler and 2 chase nipples. So No way to put a bond bushing on it. I will be using my own KOs so no concentric. From what I see in 250.97, I can do this as the chase nipple will seat flush to the Panel can (No Paint).
Also im confused if you ever need bond bushings if I run a Bond jumper from the 480v panels ground bar to the grow panel ground lug. I would also think that length would play a role, less than 24"? A chase nipple is only like a 4" raceway.
I have to do it in 12 greenhouses so I want to get it right.
Thanks for any help!