Re: bond bushings
Iwire...thankyou for your responce to my question...
A fault on the line side of a service disconnect may not open the primary fuse, and if it doesn't something is going to burn clear.
In the Soares book on grounding (9th edition) on page 81,"Bonding of Service-Conductor Enclosures", they state that the bondings purpose is so enclosures won't become isolated electrically and become a shock hazard. Then in the last sentence they say...
"The bonding also provides a low-impedance path for fault current so the fuse or circuit breaker on the line side of the electric utility transformer will open or operate."
All I was trying to say with the bonding on 1 end of that nipple between the meter can and the panel, is that there could be a fire hazard under certain circumstances, as I have described.
shortcircuit2