Bond bushings

Status
Not open for further replies.

olly

Senior Member
Location
Berthoud, Colorado
Occupation
Master Electrician
Can someone either answer my question or point me where and when in Art 250 bond bushings are required.

If you have LFMC with #1 conductors in-between two panels does both ends need a bond bushing or just one?
 
Bonding bushings may be required to comply with 250.92(A)(B), 250.97, possibly in your specific case as mentioned 250.118(6). One end of raceway required to be bonded.
 