Thanks in advance. (3) part question:
1. Do I need to show a separate Bond Commercial Kitchen Stainless Steel wall? I am showing metal boxes and metal faceplates on and within the SS wall.
2. Largest load in this vicinity is 50 amp 2-pole; #10 Ga CU bond size correct?
3. What would be an appropriate method of terminating a permanent bond wire to the SS?
1. Do I need to show a separate Bond Commercial Kitchen Stainless Steel wall? I am showing metal boxes and metal faceplates on and within the SS wall.
2. Largest load in this vicinity is 50 amp 2-pole; #10 Ga CU bond size correct?
3. What would be an appropriate method of terminating a permanent bond wire to the SS?