jimport
Senior Member
- Location
- Outside Baltimore Maryland
- Occupation
- Master Electrician
An inspector told me today that connecting the ground from an SER cable to a lug on the disconnect enclosure was not the preferred method. He said I should have used the lug next to the neutral as it did not depend on the bond screw to clear the fault. The lug next to the neutral was not large enough for the ground so I used the supplied lug in the threaded hole per manufacturers instructions. He also said I should have grounded to the Line side of the neutral buss, not the bottom lugs on the buss. This was on a Square D QO disconnect for a 200 A service. As the buss is continuous I do not see how this would matter.
Could someone tell me how UL would list this? What is the ampacity requirement for a bond screw?
Could someone tell me how UL would list this? What is the ampacity requirement for a bond screw?