I just had a phone coversation with "tech support" on a generator manufactured in China regarding the neutral to ground bond in their generator and "how" I might break that bond so the generator could feed a home.
WHY did I call tech support? This was a 13000kw duel fuel generator that a customer got for his home and there is nothing in the owners manual about breaking the bond to float the neutral.
I mean, I knew what to do...and I did the continuity test between N&G on the receptacle and it was bonded. There was guidance in the instructions to install a ground rod in the instructions with a warning of electroction hazard if not done.
Well the guy is trying to tell me that the neutral "is floating". I say that I tested N-to-G and it is NOT floating. He goes on to explain that it is floating with regard to the "earth".
I say "I want to connect to a home and need to float the generator neutral and what do you recommend because there is nothing in the manual?" He tells me to drop the equipment grounding conductor in the cord between the generator and the home inlet. Bingo! Exactly what we concluded in this discussion.
I would say this arrangement would require a GES at the SDS and I was thinkin to jus drop a ground rod where the gen-set is used with a GEC ready to quick connect.
Anyone see any hazard or Code violation with this arrangement?