Exception No. 2 works if there's a system bonding jumper at the "first disconnecting means", as well as at the SDS. So that works if the transfer switch is the service equipment, but doesn't comply if the transfer switch is downstream of the service.250.32(B) disallows this... but the Exception No. 2 may permit no EGC
Cheers, Wayne