I have building with a 277/480V service.
from the main 277/480V Distribution Panel (PanelA)
i am feeding a Delta-Y Step down transfromer for 120/208V Lighting loads. I am running a Equiptment grounding conductor with the Supply Conductors to the transfromer. In the Transfromer i will bond to the Transfromer Housing and to the Equiptment Grounding conductor running to my first 120/208V distribution Panel(Panel B.)
A Grounded Nuetral Conductor will also Feed Panel B. for the centertap of the low side.
As Far as i understand I need to bond the Center tap of the Y side to the Equiptment ground at some point. Correct?
Does it matter if i Bond at the transfromer or at panel B.
normaly the nuetral and ground are bonded only at the frist point of disconnect to a building. but i guess in a situation like this we have an exception. Correct?
from the main 277/480V Distribution Panel (PanelA)
i am feeding a Delta-Y Step down transfromer for 120/208V Lighting loads. I am running a Equiptment grounding conductor with the Supply Conductors to the transfromer. In the Transfromer i will bond to the Transfromer Housing and to the Equiptment Grounding conductor running to my first 120/208V distribution Panel(Panel B.)