ramsy
NoFixNoPay Electric
- Location
- LA basin, CA
- Occupation
- Service Electrician 2020 NEC
What about 250.52(B)?
(B) Not Permitted for Use as Grounding Electrodes.
The following systems and materials shall not be used as
grounding electrodes:
(1) Metal underground gas piping systems
Allow me to try post #10 again:
While few basements exist here, and few gas pipes are underground on "customer side" of gas meter, my jurisdiction treats customer side gas pipes as a Grounding Electrode System (GES) to be bonded per 250.104(B), even if just by appliance EGC, however, "utility side" of gas meter is prohibited from bonding per 250.52(B)(1).
If black pipe in LittleBill's basement is a utility-side gas line, my jurisdiction says bonding is prohibited per 250.52(B)(1).