brantmacga said:
i do a lot of fiberglass jobs and don't put any bonding grid in. Usually, there's no bonding whatsoever because 95% of them don't install handrails anymore and both of my fiberglass pool contractors use fiber optic or LED pool lights; the small surface area of those fixtures makes them less likely to leak on the curved surface of the shell.
at my last CEU code update class, the instructor said we are supposed to be installing a grid, and also wrapping the shell of the pool w/ #8 copper.
You might be doing it right, you might be doing it wrong. . It depends on which of 3 NEC options applies right now in your municipality, '05NEC, '05NEC with TIA, or '08NEC. . Then you need to separate your shell answer from your 3 possible perimeter answers. . Your perimeter question must be answered separately from your shell question.
'05 shell contour
'05 with TIA shell contour
'08 shell contour
'05 paved perimeter
'05 unpaved perimeter
'08 perimeter [all]
The following is for no metal in the pool and no rebar under the pool and no metal in the perimeter
'05 shell contour
You're in violation. . You
must add a grid under the 100% nonmetalic pool shell
'05 with TIA shell contour
You're OK, no bonding under the 100% nonmetalic pool shell required
'08 shell contour
You're OK, no bonding under the 100% nonmetalic pool shell required
'05 paved perimeter
You're in violation. . You
must add a grid under the 3 foot 100% nonmetalic paved perimeter of the pool. . Check with your inspector to see if he'll accept wire mesh
'05 unpaved perimeter
You're OK, no bonding under the unpaved perimeter required
'08 perimeter [all]
You're in violation. . You
must add a grid
OR a loop under the 3 foot perimeter of the
all pools, no exceptions. . If you choose the loop option, its installation must follow some very specific specs that are found at 680.26(B)(2)(b) and if the pool
does have metalin the shell, that loop must attach to the shell at 4 uniformly spaced tails, see 680.26(B)(2).