Hmmmm, feel free to knock me down if I’m wrong but:
NEC 250.4(A)(3) states that metal parts of electrical equipment must be connected to an effective ground-fault current path. However, since PVC is non-metallic, it does not create a conductive path that requires grounding or bonding. The pull box is not carrying current or part of an electrical grounding system. If metallic conduit were used, bonding would be required, but with PVC, it is not necessary.
NEC 250.96 applies only when enclosures are required to be grounded per other NEC rules, such as 250.86 or 250.110. It requires bonding of metal enclosures if they are likely to become energized or if they are part of the grounding system. Since the pull box is simply a pass-through and is not likely to become energized, bonding is not required. Additionally, because PVC conduit is used, the box is not part of a grounding system. Bonding would only be required if metallic conduit (EMT, IMC, RMC) were connected, which is not the case here.
NEC 314.4 states that metal boxes must be grounded if they contain circuits required to be grounded. However, this applies only if the box itself is required to be grounded, which it is not in this situation. If conductors were spliced or terminated inside the box, grounding would be required, but since it is just a pass-through with PVC conduit, that requirement does not apply. If metallic conduit were used, grounding would be required, but PVC is non-metallic and does not require bonding.
Since the box is only a pass-through with PVC conduit entering and exiting, and there are no splices, terminations, or metallic conduits attached, bonding is not required. However, if conductors were spliced or terminated inside, or if a metallic conduit such as EMT, IMC, or RMC were used, bonding would be necessary. The NEC sections referenced, 250.4, 250.96, and 314.4, do not require bonding in this situation……..or am I wrong?