I'm a bit confused about bonding a wooden shed utilizing a sub-panel. 250.32A which states: "Buildings or structures supplied by feeders or branch circuits shall have a grounding electrode or grounding system..."
This is a large wooden structure located ~25' from the main panel in the residential home. The main service entrance panel has the standard 2 grounding electrodes, and is feeding a sub-panel in the shed. The shed does not have any metal plumbing or other metal structural components. The sub-panel will serve single phase cord and plug type equipment, and a mini-split heat pump unit. The shed's sub-panel will have 3 conductors w/ additional ecg.
There is an exception to 250.32A, "a grounding electrode shall not be required where only a "single" branch circuit, including a multi-wire branch circuit, supplies the building or structure, and the branch circuit includes an equipment grounding conductor..."
Now, would you:
1. install a separate grounding electrode for the shed?
2. run a bonding wire outside the underground conduit from the main panel's existing rod to the new sub-panel?
3. not worry about the bonding this structure because there is not metal in the structure other than the sub-panel itself or because of the exception? I don't think this exception applies because this structure will have several circuits.
Thanks.
Now, would you:
Thanks.