For 38 years I've worked as an electrician and ALWAYS drove a ground rod next to a transformer and bonded XO, and then the "first point of service" so that any ground fault would return to the first point of service.
Recently, while working on a new service here at the college, one of my crew members contacted this forum to get clarification of where to bond the neutral for this new service. He was instructed not to bond the "first point of service" if the transformer neutral was bonded.
This leads me to believe that the fault now has to go back to the OCP serving the transformer and I don't understand that.
Case in point is the power company. They build a transformer bank for your service and bond their new neutral to ground. You then connect your service to this feeder and bond your "first point of service". There is an obvious contradiction here that I would appreciate anyone clearing up for me.
Thanks for your time.
Recently, while working on a new service here at the college, one of my crew members contacted this forum to get clarification of where to bond the neutral for this new service. He was instructed not to bond the "first point of service" if the transformer neutral was bonded.
This leads me to believe that the fault now has to go back to the OCP serving the transformer and I don't understand that.
Case in point is the power company. They build a transformer bank for your service and bond their new neutral to ground. You then connect your service to this feeder and bond your "first point of service". There is an obvious contradiction here that I would appreciate anyone clearing up for me.
Thanks for your time.