Walt Kaminskas

New member
Location
New Jersey
Question;
Is #6 THHN, THWN wire and larger, stranded, green in color, rated for equipment bonding and grounding in a free air installation, exposed to the elements, but not subject to physical damage?
 
300.6(C)(1) Exposed to Sunlight Where exposed to sunlight, the materials shall be listed as sunlight resistant or shall be identified as sunlight resistant.
 
I'm not sure I understand the question. EGC's when installed must be run with the circuit conductors.
 