I'm confused about the requirement to bond around concentric KO's on enclosures where the voltage to ground exceeds 250 volts. Is the bonding bushing required to bond the enclosure or the raceway?
Here's one example:
I have an EMT branch circuit conduit run from a punched KO in a panelboard to a junction box with a concentric KO in the JB. Within the conduit is a EGC that terminates at the panel and is connected to the JB. Is a bonding bushing required at the JB?
I would say no, since the conduit is bonded at one end by the connector installed in the punched KO at the panel and the JB is bonded by the EGC connected at both ends. Am I reading the requirement correctly?
Here's example #2: Same as Example #1 but the conduit has concentric KO's at both ends and an EGC within the EMT. Are bonding bushing(s) required?
Trevor
Here's one example:
I have an EMT branch circuit conduit run from a punched KO in a panelboard to a junction box with a concentric KO in the JB. Within the conduit is a EGC that terminates at the panel and is connected to the JB. Is a bonding bushing required at the JB?
I would say no, since the conduit is bonded at one end by the connector installed in the punched KO at the panel and the JB is bonded by the EGC connected at both ends. Am I reading the requirement correctly?
Here's example #2: Same as Example #1 but the conduit has concentric KO's at both ends and an EGC within the EMT. Are bonding bushing(s) required?
Trevor