charlie
- Indianapolis
Re: Bonding at Reducing washers
Tom, do you have the 2004 version of hte UL White Book? I have the PDF version and it is is mine.
This category covers supports for outlet and flush device boxes; fittings for use in or on outlet and flush device boxes, such as knockout reducers, seals and insulating inserts, and cord grip attachments; service entrance heads for rigid conduit or electrical metallic tubing; cable riser supports; and bushings for use on the ends of rigid or flexible conduit, or electrical
metallic tubing, where a change to open wiring is made.
Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70, ??National Electrical Code.
This seems pretty clear to me.