I would think if you are pulling an egc with the ccc, then no bonding bushing is required. If the emt is used as egc, then my guess is yes.
Here is a good article from UL's website on the subject.
http://www.ul.com/global/documents/...nical/ul_BondingAroundConcentricKnockouts.pdf
excellent reference
250.97 takes us to 250.92(B) except B(1). The highlighted section is brand new to 2011.
(B) Method of Bonding at the Service. Bonding jumpers meeting the requirements of this article shall be used around impaired connections, such as reducing washers or oversized, concentric, or eccentric knockouts. Standard locknuts or bushings shall not be the only means for the bonding required by this section but shall be permitted to be installed to make a mechanical connection of the raceway(s).
How about 250.97 EX. 4
From UL
GROUNDING
Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70, "National Electrical Code." Reducing washers are intended for use with metal enclosures having a minimum thickness of 0.053 in. for non-service conductors only. Reducing washers may be installed in enclosures provided with concentric or eccentric knockouts, only after all of the concentric and eccentric rings have been removed. However, those enclosures containing concentric and eccentric knockouts that have been Listed for bonding purposes may be used with reducing washers without all knockouts being removed.
Therefore I don't believe I need to read or be confused by this;(2) Connections utilizing threaded couplings or threaded
hubs on enclosures if made up wrenchtight
(3) Threadless couplings and connectors if made up tight
for metal raceways and metal-clad cables
(4) Other listed devices, such as bonding-type locknuts, bushings,
or bushings with bonding jumpers
Thats not 'one of the methods' I need be concerned with.(B) Method of Bonding at the Service. Bonding jumpers
meeting the requirements of this article shall be used
around impaired connections, such as reducing washers or
oversized, concentric, or eccentric knockouts. Standard
locknuts or bushings shall not be the only means for the bonding
required by this section but shall be permitted to be installed
to make a mechanical connection of the raceway(s).
Agreed?From UL
GROUNDING
Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70, "National Electrical Code." Reducing washers are intended for use with metal enclosures having a minimum thickness of 0.053 in. for non-service conductors only. Reducing washers may be installed in enclosures provided with concentric or eccentric knockouts, only after all of the concentric and eccentric rings have been removed. However, those enclosures containing concentric and eccentric knockouts that have been Listed for bonding purposes may be used with reducing washers without all knockouts being removed.
Yes but remember my quote is from 2011. Perhaps the other quote will change when the new UL book comes out.These two documents do seem to be in conflict.
Dennis, did you see post 30?
So guy's let me get this straight, concentric or eccentric knockouts are ok on load centers to bond the conduit for branch circuits, but they are not ok for grounding a disconnect enclosure that for the most part have virtually the same type of concentric or eccentric knockout?
Remember, we're focused on concentrics/eccentrics on this discussion - a hole without concentrics/eccentrics surrounding it do not need the bonding bushing.Several years ago we discussed this issue to death here, and at one of my IAEI Western Sectionals it was a big topic, that both resulted in that for other then service conductors or GEC they were acceptable bonding means, now the code has changed this? I missed this code change
Because that post was devoted exclusively to a box that was listed for concentric use. Now, enter the cabinets, gutters, and switches that are not listed for that use. They cannot use the exception, so they go straight to 250.92 for instructions.Now that makes sense. Now why this change to 250.92 if it makes no never mind.
How does 250.92(B)(4) apply to reducing washers. Other listed devices such as bonding type locknuts, bushings, or bushing with bonding jumpers. Not sure I see reducers in this scenario but I see how one might.Because that post was devoted exclusively to a box that was listed for concentric use. Now, enter the cabinets, gutters, and switches that are not listed for that use. They cannot use the exception, so they go straight to 250.92 for instructions.
250.92(B)(4) would allow the reducing washer as a "fitting" for those "dirty" boxes.
What about if you have a ground fault in your conduit?
If not in this scenario, then what scenario would the special listing (over 250V) kick in?Not sure I see reducers in this scenario but I see how one might.