Pierre C Belarge
Senior Member
- Location
- Westchester County, New York
250.97 is the section that we are referencing.
In the main body of language in the paragraph, it gives us the requirements to follow.
There is an exception that we can reference. It states different information that we are permitted to follow.
Read the first paragraph of the exception.
Also, the reference in the main body of language for 250.92 is referencing 250.92(B), not (A).
"...Bonding jumpers meeting the other requirement of this article shall be used around concentric or eccentric knockouts that are punched or otherwise formed so as to impair the electrical connection to ground."
Most of the equipment manufactured today does not impair the connection to ground. See (BGUZ) & (QCIT) of the UL White Book
As Augie mentioned in one of his posts, additional bonding would not be required.
P.S. we are not talking about the equipment ground conductor installed in the raceway.
In the main body of language in the paragraph, it gives us the requirements to follow.
There is an exception that we can reference. It states different information that we are permitted to follow.
Read the first paragraph of the exception.
Also, the reference in the main body of language for 250.92 is referencing 250.92(B), not (A).
"...Bonding jumpers meeting the other requirement of this article shall be used around concentric or eccentric knockouts that are punched or otherwise formed so as to impair the electrical connection to ground."
Most of the equipment manufactured today does not impair the connection to ground. See (BGUZ) & (QCIT) of the UL White Book
As Augie mentioned in one of his posts, additional bonding would not be required.
P.S. we are not talking about the equipment ground conductor installed in the raceway.