Given CAT5 data and telephone wiring in non-plenum tray in a commercial installation:
725.56 (D)(1) says reclassify data as communications cable and install per Art 800.
800.110 says install per Chapter 3.
392.7 (A) says ground per 250.96
250.96 says trays THAT ARE TO SERVE AS GROUNDING CONDUCTORS shall be bonded...
CAT5 wire runs do not require an equipment grounding conductor, so do I need to bond when run in tray? Inspector says yes...
725.56 (D)(1) says reclassify data as communications cable and install per Art 800.
800.110 says install per Chapter 3.
392.7 (A) says ground per 250.96
250.96 says trays THAT ARE TO SERVE AS GROUNDING CONDUCTORS shall be bonded...
CAT5 wire runs do not require an equipment grounding conductor, so do I need to bond when run in tray? Inspector says yes...