Smart $ Esteemed Member Location Ohio Dec 16, 2014 #21 jap said: ... Would a #12 Ground Stinger not do its job on a 30 Amp circuit? Click to expand... Probably.... But there's that fringe area of the #12 that wouldn't be there with a #10...
jap said: ... Would a #12 Ground Stinger not do its job on a 30 Amp circuit? Click to expand... Probably.... But there's that fringe area of the #12 that wouldn't be there with a #10...
J jap Senior Member Occupation Electrician Dec 17, 2014 #22 infinity said: I wouldn't call anyone who would do that competent.hmy: Click to expand... You wouldn't have to call them anything, since if you opened up a panelboard (not knowing that anything was changed) and seen #10'S connected to a 30 amp breaker you'd probably not think twice about it.
infinity said: I wouldn't call anyone who would do that competent.hmy: Click to expand... You wouldn't have to call them anything, since if you opened up a panelboard (not knowing that anything was changed) and seen #10'S connected to a 30 amp breaker you'd probably not think twice about it.
J jap Senior Member Occupation Electrician Dec 17, 2014 #23 But I agree with the earlier post of it all depending on what the circuit is feeding downstream. JAP>
But I agree with the earlier post of it all depending on what the circuit is feeding downstream. JAP>