Re: Bonding Conduit At Utility Pole
romeo
I read your most recent plea, and will try to shed a bit of light, and some sorrow, on your predicament.
The utility system is generally exempt from the NEC, and 250.66 probably does not apply in this case, to any bonding connection being made to the utility system. I say that because if the utility installed the conduit, clearly 250.66 couldn't apply at all. I think the district engineer is probably right.
The NESC, the utility Code, does require equipment frames, enclosures, and all nonenergized conducting components within reach, to be bonded to create a low impedance path for fault currents to flow and devices to operate. I don't have a current NESC in front of me, but that was quoted from 93 C 7 in the 1993.
Now the really bad news. If the utility transformer is a large kva unit, say 50 kva or up, it is possible that the cutout fuse will never blow at all. I have seen numerous secondaries laying on the ground, sparking away. Having an isolated piece of conduit bonded to a pole ground will do little to increase the fault current in a significant number of instances.
Not to dispair, If I was the utility engineer, and you asked me about the specific grounding requirements, you should check the section against the current NESC, I would at least think a little more before I offered answers. You should be able to make the NESC stick.
Jim T
romeo
I read your most recent plea, and will try to shed a bit of light, and some sorrow, on your predicament.
The utility system is generally exempt from the NEC, and 250.66 probably does not apply in this case, to any bonding connection being made to the utility system. I say that because if the utility installed the conduit, clearly 250.66 couldn't apply at all. I think the district engineer is probably right.
The NESC, the utility Code, does require equipment frames, enclosures, and all nonenergized conducting components within reach, to be bonded to create a low impedance path for fault currents to flow and devices to operate. I don't have a current NESC in front of me, but that was quoted from 93 C 7 in the 1993.
Now the really bad news. If the utility transformer is a large kva unit, say 50 kva or up, it is possible that the cutout fuse will never blow at all. I have seen numerous secondaries laying on the ground, sparking away. Having an isolated piece of conduit bonded to a pole ground will do little to increase the fault current in a significant number of instances.
Not to dispair, If I was the utility engineer, and you asked me about the specific grounding requirements, you should check the section against the current NESC, I would at least think a little more before I offered answers. You should be able to make the NESC stick.
Jim T