Inspector is requiring ductwork and metal gas pipe in crawl space to be bonded.
In past jobs I have never been required to do this since the EGC from the furnace circuit sufficed.
He is saying that it could become energized and that the #14 EGC is undersized.
Is it acceptable to just bug onto the GEC conductor and hit both the black iron pipe and the sheet metal?
Thanks