Hey, gang. I looked at a kitchen hood system to price wiring it, and the customer mentioned that I had to bond ("run a ground wire") around the flexible section of gas pipe supplying the cooking equipment.
There is about 45' of the yellow-coated flexible gas pipe between the source end (where it comes off of a larger pipe) and the solenoid valve, which then feeds three cooking appliances via about 5-6' of pipe, nipples, and tees.
There is no electrical equipment at all (excluding the light) under the hood. The only thing 'likely to energize' the pipe is the solenoid valve for the suppression system, and the valve has an EGC.
My questions are:
1. Do I need to run such a wire? Is this requirement separate from the typical bonding requirements
2. If so, should this wire connect the short section of piping to the other end of the yellow flex, or to the service EGC?
3. What kind, size, insulation, etc. must this wire consist of?
4. Can a typical brass/bronze pipe clamp be used on the pipe?
5. Can I simply nylon-wire-tie this bonding wire along the flex, since it's being used to parallel the flex?
Danke,
There is about 45' of the yellow-coated flexible gas pipe between the source end (where it comes off of a larger pipe) and the solenoid valve, which then feeds three cooking appliances via about 5-6' of pipe, nipples, and tees.
There is no electrical equipment at all (excluding the light) under the hood. The only thing 'likely to energize' the pipe is the solenoid valve for the suppression system, and the valve has an EGC.
My questions are:
1. Do I need to run such a wire? Is this requirement separate from the typical bonding requirements
2. If so, should this wire connect the short section of piping to the other end of the yellow flex, or to the service EGC?
3. What kind, size, insulation, etc. must this wire consist of?
4. Can a typical brass/bronze pipe clamp be used on the pipe?
5. Can I simply nylon-wire-tie this bonding wire along the flex, since it's being used to parallel the flex?
Danke,