chevyx92 said:And I have done many and never been required to bond any of that. So go figure.
I figure your inspectors are slack. :grin:
chevyx92 said:And I have done many and never been required to bond any of that. So go figure.
Dennis Alwon said:You are correct but the job will fail unless someone bonds it. No heating guy or plumber is allowed to enter our panels so there is the catch 22.
It needs to be bonded-- I never said the NEC requires it.
BDB said:One of our local AHJ's has told me to not bond the gas in some apartments we are doing. The gas is all yellow TracPipe, no iron pipe anywhere. We are also required to keep all wiring at least 2" away from the gas pipe. I've no idea if this is a bad idea, but it's what he wants, and so it's what we do![]()
BDB said:One of our local AHJ's has told me to not bond the gas in some apartments we are doing. The gas is all yellow TracPipe, no iron pipe anywhere. We are also required to keep all wiring at least 2" away from the gas pipe. I've no idea if this is a bad idea, but it's what he wants, and so it's what we do![]()
iaov said:I believe so. If the black pipe coming into the building is bonded already there is no need to mess with the yellow stuff IMO. As a common sense thing if there are no electrons running about here, and it is not" likely to become enegized"(words of the BooK), no bonding equired.
Here's what I'm saying:Dennis Alwon said:Isolated how. If it is connected to the gas piping(black piping) and that pipe is bonded according to 250.66 then you don't need to go any further. You cannot rely on the egc to bond this pipe.
LarryFine said:Dennis, did you get that I'm only asking about bonding a 6' hunk of pipe asembly, and not the building's gas-pipe system?
Okay, lemme try again.Dennis Alwon said:Isn't the flex pipe connected to the black pipe somewhere? I don't see how this 6' flex is connected to nothing. Either way it must be bonded. If you bond the black pipe then you are bonding the flex if they are connected to each other.
I must be missing something-- maybe a brain I don't know...:-?
CSST gas piping systems shall be bonded to the electrical service grounding electrode system at the point
where the gas service piping enters the building. The bonding conductor size shall be not less than #6 AWG
copper wire or equivalent.
Larry Fine said:So, I was only told this new short section of pipe has to be bonded. It makes more sense to me to run this required bonding wire from this pipe to the old pipe at the other end of the flex, similarly to an external EGC on a length of electrical flex, than to the electric service.
No. Once more:Dennis Alwon said:You keep saying that you only have 6' of flex but you actually have 45' plus the 6'. The existing 45' should have been bonded but probably wasn't.
LarryFine said:No. Once more:
The existing piping is old, big, and of unknown length. It's probably there for the original heating of the building. The 45' is the length of the new CSST, and the 6' is the length of hard pipe at the kitchen end of the new run of flex.
Got it now? Old pipe unknown. New flex, new 6' of pipe assembly to serve the three new appliances. I was told that we have to bond the new 6' length of hard pipe, so it doesn't rely on the conductivity of the new 45' of CSST.
My take is that you need to ensure the existing hard pipe is bonded to the electrical service ground in order to protect the new CSST (according to the manufacturers). As I understand it, this can be done anywhere on the hard pipe that is convenient, since the hard pipe has low impedance.LarryFine said:The existing piping is old, big, and of unknown length. It's probably there for the original heating of the building. The 45' is the length of the new CSST, and the 6' is the length of hard pipe at the kitchen end of the new run of flex.
That's a new one to me, but once you have bonded the existing hard pipe, you can then jumper around the CSST, no need to go back to the service with that jumper. Since you need to bond the existing hard pipe anyway, your concern that jumpering around the CSST increasing the hazard if the hard pipe is unbonded will be mute.LarryFine said:I was told that we have to bond the new 6' length of hard pipe, so it doesn't rely on the conductivity of the new 45' of CSST.