Bonding for underground vault

Status
Not open for further replies.

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
a two hole terminal crimp lug, bolted to the door, using corrosion paste?
i believe a meshed grounding wire of proper size can be used, better for flexing as that door opens and closes.
 

Jim1959

Senior Member
Location
Longmont, CO
I would recommend either a flexible strap, or a more flexible conductor, like welding cable. The wire connection may not hold up to repeated opening and closing of the lid.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Over here we get nailed for not using a DB rated or some sort of otherwise corrosion resistant lug outdoors. That said, I've never grounded a vault lid either though....:ashamed1:
 