The only time you would bond the gas line with a grounding conductor from your service is if there is CCST type flexible gas line also attached to the metal gas line. And that would only be required to be #6.
Otherwise it is effectively bonded by the branch circuit grounding conductor that attaches to the equipment that is also attached to the gas line ex. a furnace.
Gas code does not allow you to treat a gas line as a grounding electrode, even if it were to be metallic underground to your home. Although the process of bonding in itself would create this condition it' s just not recognized as a grounding electrode.
If anything maybe the inspector is recommending it be bonded in the event in the future there could be CCST flex line installed, still #6 is all that's needed.