Are you allowed to Do the bonding from a sub panel as long as the equipment ground feeding the sub panel is sized properly. If this is ok where is it in the code.
Sorry,,,I didn't try to sound harsh, but I can't stand these guys quoting articles that have little impact on the actual decision making. I pull permits in MY NAME,,,I deal FIRST HAND with the inspectors and if your job has CSST on it, it must be bonded by the man. instructions. or you will NOT get your inspections passed. NO MATTER what the NEC says. The EGC will not be accepted. No matter how many times you recite the code article. and about the spelling,,,,,,,,WE'RE NOT IN ENGLISH CLASS
The NEC is not the only book involved here. The IBC )
First of all CSST is not installed by electricians therefore it's not the electricians responsibility to bond it. That the plumbers job and bonding requirements are part of the CSST listing which has nothing to do with the electrician.
The NEC is not the only book involved here. The IBC and UBC both mandate gas pipe bonding per manu. instructions.
Actually the IBC has no such mandates for gas piping. The IFGC (International Fuel Gas Code) regulates fuel gas piping.
Chris
How dare you bring facts into the argument! :smile:
I completely agree. HVAC guys and plumbers are using CSST at record paces and expect us to bond the junk as part of our bid. Not happening on the jobs I do. If they want to pay me to do the bonding, I'm on it.
So do you include in your bid the price of bonding metallic water piping that you didn't install? Or do you expect the plumber to do that? Or do you specifically call out that you will bond water piping and any pipe types are extra cost?
Wow, that was harsh. :roll:
Most people base their answers to questions here on the NEC as that is the most widely used electrical code. (Not to mention that it is the basis for this forum)That being the case The NEC does not require any gas piping to be bonded unless it is likely to become energized. As far as I am concerned if I wire a building to the current NEC the gas piping is not likely to become energized and therefore needs no bonding.
If your area has adopted other codes that is fine FOR YOU but it does not apply to everyone.
In the real world where I am I don't wire to "what the inspectors are asking for nowadays", I wire to the code that is in effect.
By the way, the word is "advice". If you want people to take it you should at least be able to spell it.:grin:
Mark,
I don't see how your argument is fair. The water pipe is specifically required by Article 250 of the NEC to be bonded, CSST gas pipe isn't. The additional bonding requirement for CSST is part of the listing from the manufacturer of the pipe therefore isn't not part of the electrical code. Comparing the too is like comparing apples and oranges.
The NEC is not the only book involved here. The IBC and UBC both mandate gas pipe bonding per manu. instructions. Which means, If the job has ALL STEEL PIPE,,,,,the bond can be sized accordingly as noted above and the EGC will cover you. HOWEVER,,,,if there is ANY CSST on the job(even a short piece behind the stove,,,THEN you CANNOT size the bond by the EGC,,,,,it will have to be a minimum of a #6 copper,,,,,and one manu, (wardflex) mandates the bond to be the same size as the GEC. And yes, it must go to the service pane and not subpanel. Don't listen to the guys that quote the NEC off the top of their head. Once you get into the REAL world the inspector uses many other sources besides the NEC. Take this advise from someone who ACTUALLY wires house for a living in many different counties and I know what inspectors are asking for nowadays.(at least in VA)