hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
Paul, here in Indiana we are not even required to take the CSST bonding back to the service, it was recognized that the whole problem with CSST was the current from lightning, and just bonding the one end of the CSST will not prevent this, we are required to bond around it meaning the a #6 conductor or larger has to be run with the CSST to bond both ends together. what help will a bond to the service do if lightning hits a flue or chimney and comes down to this CSST pipe and tries to flow over it back to the GEC of the service. without a bond in parallel with the CSST it can cause the CSST to fail? this has nothing to do with bonding to the service but the bonding of each end of the CSST.