As pointed out by @zbang CSST and flexible appliance connectors are two different things and one is not to be used in place of the other.
CSST is used (or can be used) on fixed appliances, water heaters , boilers, furnaces but not to be used on stoves and dryers that are sometimes moved for cleaning, thats where the flex connectors are used
I am also a licensed gas fitter. I never herd of any bonding/grounding requirements with the flex connectors. Pipe dope etc I don't believe has any bearing as the gas piping is bonded....not to be used as a grounding electrode.
CSST is another matter. Some types are approved for bonding with no jumper around them "counter strike" is one brand I have seen. If the CSST is not approved for bonding then a jumper should be installed around it. At least thats my take