PietjePuk
- Calgary, Alberta, Canada
- Electrical Engineer
I have a question that I don't have fully answered and was wondering if you could provide some clarification or your insight on if at all possible.
I have a question on bonding/grounding:
I have done some searching, and compiled a short document with some, to me, controversial information.
My question is - does every bolted piece in the structure (enclosure and radiator structure) need to be bonded with methods indicated in document (bond strap, washers, clean unpainted surfaces), or only any pieces where there is a chance of it becoming energized by shorts/worn/broken cables? Obviously all control panels, cabinets, etc will have to be bonded as is common practise, but my question is more about the structure and wall panels of the enclosure and the radiator system on top.
I have never seen a structure where every pieces of metal in a frame structure is bonded.
- Natural gas powered generator (5MW) inside a structure that encloses it, permanently anchored on a concrete pad on a site
- Generator produces 13.8kV but the MV lines go directly from the generator to a switchgear (GCB, transformer etc) 6ft outside the skid
- 480V source is brought in from the switchgear to power auxiliary loads (rad, ventilation, coolant pumps, oil pumps, airconditioning, heating,etc and other 120V auxiliaries such as lights, receptacles etc)
- The structure is a base frame with bolted pieces to it to form the structure around it (bolted uprights, corners, etc).
- Aluminum panel sections get bolted to the structure to form the walls and roof
- All cables inside the structure are run in metalic trays along the sides of the structure
- A bolted frame rad with motors and sensrs etc is bolted to the top
- Some of the bolted frame pieces are 2ft in length
- The trays and tray systems are all bonded and grounded.