RUWired said:
As soon as they improve this fiber optic, we'll be able to see what the OP is saying.
But untill then i am only assuming that he is installing a new grid with two gen sets and one transfer switch.
Rick
I was thinking about this on the way out, and there's just a lot of different ways to see it. I do apologize for saying you guys were jumping to conclusions, that was not cool.
The two different ways I can see this are two generators connected to a pole of the MTS, and some kind of utility power connected to the other pole. The other is two generators connected to either pole of the MTS, which could change things too.
Lately I've been dealing with a lot of redundancy, and so a pair of generators on the same pole wouldn't have surprised me - but in retrospect, you guys are probably right about the configuration.
So, starting at the top:
benaround said:
Gensets have neutrals, so what is a delta ground system?
The only use of that term I know of is the practice of driving three ground rods in close proximity to each other in a triangular pattern. I don't see the relevance here, unless the OP intends to connect to drive one set of these rods at the MTS and call it a day, to avoid driving rods at the generators.
If we assume that both generators are two different SDSs that supply the MTS, and also assume that OCPD is present at the generators before they feed the transfer switches, then I would say that is the reverse of what's required in the NEC. 250.30(A)(7)(x.1) would require the rods be connected at each generator, at the disconnecting means provided. Grounding electrodes at the MTS would not be required, unless we consider it screwed to a detached structure governed by 250.32(A).
If we were to assume they are two SDSs, then the neutrals would have to be switched, and the bonding would take place in each generator. Each generator would be an SDS requiring a GES of their own.
If we were to consider the pair one SDS, then the neutrals could be connected together (but separate from the EGCs) inside the MTS. Then, one generator would retain it's bonding jumper and the other wouldn't. The generator with the bonding jumper in it would have a GES, and the other one wouldn't.
jrannis said:
Ignore the bond inside of the generator.
I don't see how this is a code compliant approach.
jrannis said:
Connect the ground at the MTS neutral if is considered your "Service" disconnect.
If there are one or two SDSs and no service, then there is no service disconnect. There is a disconnect required by 445.18 to be located in the generator. If there's a disconnect at the generator, then it would have to be ahead of the transfer switch, and that would eliminate the option of the SDS Grounding Electrode System (GES) originating at the MTS.
jrannis said:
Its possible that someone could bring in a generator that doesnt have the neutral connection inside of the generator.
jrannis said:
You cant be sure of what kind of equipment someone might roll up with or who will be asked to connect it to the building.
Its best to check the frequency, voltage, breaker size and KW of the unit along with the rotation if necessary and not be overly concerned about how the netural is connected to the generator head.
It will not matter to you.
We are not responsible for the grounding mistakes of those that come after this, and this is encouraging a 250.6 violation to protect against those mistakes, IMO.
That's my take on the situation, jumping into the conclusions game. Thoughts?