Re: Bonding -Grounding the Neutral
Stew
It seems to me it says it is permitted to be attached not required to be attached?
You are exactly right, it is saying permitted to be attached. The grounding electrode conductor and the grounded conductor are required to be connected to the same point ( neutral bar) and it is a permissive statement if you do not land the grounding electrode conductor on the same bar as the neutral you have a permissive statement in 250.24 allowing the grounded electrode conductor to land on a bar(equipment grounding) that the neutral is not connected to as long as there is a main bonding jumper in the form of a bus-bar or wire bonding the two bus-bars together
[ March 05, 2004, 11:14 PM: Message edited by: david ]