In my mind the hub mentioned in 250.92(B)(2) is one of these:Design features
- Wide range of styles, trade sizes and materials to meet customer requirements and preferences
- Multiple certifications provide users peace of mind
- Easy installation and smooth pulling service for labor savings
- Tapered female threads for rigid/IMC conduit, NPSM male threads
- Nut with grounding screw available for added safety
- Strong, oversize nut with radial serrations is resistant to vibration, assuring flush installation and positive grounding
- Unique serrations on both nut and hub bite into metal, assuring a positive electrical ground (UL approved for use with service entrance conduit)
And when you lose those screws you replace them with ones that don't have the features mentioned.First question, are there any eccentric or concentric KO's? Next question, is the hub mentioned in 250.92(B)(2) permitted to be a Myers hub?
If the answer to the first question is yes then bonding bushing required. Second question get a little fuzzy. Eaton Myers Hub specifications say this:
In my mind the hub mentioned in 250.92(B)(2) is one of these:
As far as I know the only Myers hubs listed as grounding and bonding equipment are the ones with a tab to connect a bonding jumper, so I would say for the purposes of service bonding they are the same as a locknut.And when you lose those screws you replace them with ones that don't have the features mentioned.
Does a Myers hub and it's supplied locknut meet the same criteria as any ordinary locknut? If so then additional methods to assure bonding are needed just like for an ordinary locknut on service raceways.
I have never used any additional bonding on them other than for service raceways, which was pretty infrequent but has been done.As far as I know the only Myers hubs listed as grounding and bonding equipment are the ones with a tab to connect a bonding jumper, so I would say for the purposes of service bonding they are the same as a locknut.
That was my thought as well.As far as I know the only Myers hubs listed as grounding and bonding equipment are the ones with a tab to connect a bonding jumper, so I would say for the purposes of service bonding they are the same as a locknut.
I would say no, but that's a hotly debated subject.Is a bonding bushing required in a meter pan if using a Meyers hub made up wrench tight?