Sorry! I combined the two questions! # 20 is correct for 2nd question!yes, and? my specific question is regarding the wire labeled 'supply side equipment bonding jumper'. It seems to be mislabeled.
Sorry! I combined the two questions! # 20 is correct for 2nd question!yes, and? my specific question is regarding the wire labeled 'supply side equipment bonding jumper'. It seems to be mislabeled.
All good. The title of my post was misleading / incomplete as well.Sorry! I combined the two questions! # 20 is correct for 2nd question!
I guess they are feeders, but the code only calls them transformer secondary conductors.Agree with the second sentence, but for an SDS aren't the transformer secondary conductors also feeders? They are not service conductors, and they are not branch circuits.
Cheers, Wayne
One could argue that conductors qualifying under 240.21(C) are not tap conductors. Otherwise yes.I thought the transformer secondary conductors were considered tap conductors.
Ok I can see that.One could argue that conductors qualifying under 240.21(C) are not tap conductors. Otherwise yes.
But all feeder tap conductors are also feeder conductors.
Cheers, Wayne