bonding jumper in transfer switch

Status
Not open for further replies.
if my relocated GEC is landed on the transfer switch ground bar, and my neutral bar has a bond strap to the transfer switch cabinet, do I need a bonding jumper between the neutral bar and the ground bar? Is it ok for the cabinet to be used as the bonding jumper?
 

Buck Parrish

Senior Member
Location
NC & IN
No, It's okay for equipment grounding bar not the neutral . Not sure where the code section is. But seems like I read it at least once.
 