Re: Bonding Junction Box

250.122 (G) Feeder Taps Equipment grounding conductors run with feeder taps shall not be smaller than shown in Table 250.122 based on the rating of the overcurrent device ahead of the feeder but shall not be required to be larger than the tap conductors.
This was not a change, it was added only because many were not reading the rule correctly.
Don
 