250.106 states that these systems shall be bonded to the grounding electrode system, but does not specify how to size the bonding jumper? 250.66?
Can you explain what that means?bphgravity said:For both Class I and Class II materials...
Is a #6 jumper between a LPS elecrode and an electrical grounding electode (or GEC, buss bar, or grounding electrode jumper) a possible option?electrofelon said:... I am interested in how the actual connection will be made between the bonding jumper and the loose-braid cable of the LPS. I suppose I will just split bolt it. ...
Well, if you're secretly harboring such desires, you'll have to get back into Article 210 to try again.electrofelon said:Contrary to the way it sometimes seems George, my goal isnt to just stump you guys or try to break the longest thread record
Is a #6 jumper between a LPS elecrode and an electrical grounding electode (or GEC, buss bar, or grounding electrode jumper) a possible option?
electrofelon said:250.106 states that these systems shall be bonded to the grounding electrode system, but does not specify how to size the bonding jumper? 250.66?