Bonding metal framing???

Status
Not open for further replies.
Florida Residential Code 2004

E3302.1 Metal framing members.
Metal framing members shall be bonded to the equipment grounding conductor for the circuit that may energize the framing and be sized in accordance with Table 250.122 of the National Electric Code . For the purpose of this section, a grounded metal outlet box attached to the framing shall be permitted.

Effective 12-08-2006

In case someone is interested
 
RAYMFL said:
For the purpose of this section, a grounded metal outlet box attached to the framing shall be permitted.
"Hi. I'd like a 4" square grounding clamp, please."
 