Re: bonding metal street light poles
Originally posted by romeo: They (the utility) depend on a ground rod to trip the transformer primary fuses.
Originally posted by haskindm: There needs to be a effective ground-fault current path that does not rely on the earth as a conductor.
The transformer's primary protection is not governed by the NEC, and it may rely on the earth as a conductor. But that is because at the higher voltages associated with transmission and distribution systems, the resistance of the interface between a ground rod (or the base of the pole, perhaps) and planet Earth is not too high to prevent blowing the primary fuses. For example, if the primary side is 12,470 volts (not an uncommon rating), and if the ground rod resistance is 200 ohms, then a fault would have a current of 62 amps, and this would trip a primary fuse that is probably 10 amps or smaller.
This is in contrast to a 120 volt residential system. A ground fault that has to pass through a ground rod with a resistance even as low as 25 ohms would have a fault current no more than 5 amps, and this would not trip a 15 amp breaker.
But I think the "effective ground path on the secondary side does not rely on the earth. A fault from the hot side to the pole, let us say within the light fixture at the top of the pole, would send current down the pole, via the bonding wire to the neutral within the handhole, and immediately thereafter back to the source. That is a low-resistance path, and the resulting high current would blow the fuses on the primary side. So long as there is a transformer at each pole, and there is no feeder or branch circuit from handhole to handhole, I think it is correct to bond at each handhole.
(Edited to correct a typo.}