Re: Bonding meter can
I see what you are saying about the parallel paths between the two and with the same breath I am saying that 250.92 (A)(1) requires that the two be bonded.
250.92 Services.
(A) Bonding of Services. The non?current-carrying metal parts of equipment indicated in 250.92(A)(1), (A)(2), and (A)(3) shall be effectively bonded together.
(1) The service raceways, cable trays, cablebus framework, auxiliary gutters, or service cable armor or sheath except as permitted in 250.84.
(2) All service enclosures containing service conductors, including meter fittings, boxes, or the like, interposed in the service raceway or armor.
Read #2 can you see the requirement? This is what the NEC says it is there in black and white. I didn?t make it up.
Now 250.142 give us relief of this but it is permission and not a requirement. Being it is permissive I do not have to do it that way.
250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
(A) Supply-Side Equipment. A grounded circuit conductor shall be permitted to ground non?current-carrying metal parts of equipment, raceways, and other enclosures at any of the following locations:
(1) On the supply side or within the enclosure of the ac service-disconnecting means
250.92 is a requirement and no matter weather me you or anyone else likes it or not it is there. It will be there until a proposal is made to remove it.
As to the requirements of the utility I am not in argument about. I am only stating the requirements of the NEC.