kenaslan
Senior Member
- Location
- Billings MT
I hope this is the correct forum for this topic.
We have a vessel being installed on a concrete foundation in a refinery. Class 1 Div 2. The foundation will be 60" thick, and in direct contact with the earth, however with no rebar.
We all can agree that all rebar (Grounding Electrode) needs to be bonded. However the foundation in question has no rebar.
It seems that 250.50 implies that all foundations need to be bonded to the Grounding Electrode System and if no electrode exists then one must be added.
250.50 Grounding Electrode System
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
Section 250.50 introduces the important concept of a grounding electrode system, in which all electrodes that are present at a build-
ing or structure are bonded together, as illustrated in Exhibit 250.22. Rather than total reliance on a single grounding electrode to perform its function over the life of the electrical installation, the NEC requires the formation of a system of electrodes where multiple grounding electrodes are at the building being served. Metal structural members, metal water pipe, and concrete footings or foundations are found in many buildings and structures and are required to be integrated into the grounding electrode system if they qualify under the conditions specified in 250.52(A).
However the Structural engineer does not want to add rebar or a copper electrode to this foundation.
So my question is, must this foundation be bonded to the Grounding Electrode System?
We have a vessel being installed on a concrete foundation in a refinery. Class 1 Div 2. The foundation will be 60" thick, and in direct contact with the earth, however with no rebar.
We all can agree that all rebar (Grounding Electrode) needs to be bonded. However the foundation in question has no rebar.
It seems that 250.50 implies that all foundations need to be bonded to the Grounding Electrode System and if no electrode exists then one must be added.
250.50 Grounding Electrode System
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
Section 250.50 introduces the important concept of a grounding electrode system, in which all electrodes that are present at a build-
ing or structure are bonded together, as illustrated in Exhibit 250.22. Rather than total reliance on a single grounding electrode to perform its function over the life of the electrical installation, the NEC requires the formation of a system of electrodes where multiple grounding electrodes are at the building being served. Metal structural members, metal water pipe, and concrete footings or foundations are found in many buildings and structures and are required to be integrated into the grounding electrode system if they qualify under the conditions specified in 250.52(A).
However the Structural engineer does not want to add rebar or a copper electrode to this foundation.
So my question is, must this foundation be bonded to the Grounding Electrode System?