Bonding of copper lines in the new PEX systems

Status
Not open for further replies.

lucas chapman

New member
does the metal water piping under counters and @ water closets need to be bonded when a nonmetallic water piping (Pex) is used throughout the remainder of the building
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

No, isolated sections of copper pipe that aren't likely to be energized, don't constitute a "Metal piping system" and therefore are not required to be bonded.

Chris
 

rexowner

Senior Member
Location
San Jose, CA
Occupation
Electrician
Chris beat me to it.

See 250.104. I know it is not code, but the commentary
in the handbook under 250.104(1)(A) drove this point
home for me, based on a sensible judgment call.
 