Home inspector sited that the gas pipe (1" galvanized) that feeds a 60kva generator be bonded for lightning protection.
The generator is controlled by a ats that does not open the neutral.
This is a 400-amp service and the gas meter (not bonded) is on the opposite side of the house.
Since the ats does not open the neutral, wouldn't the feeder ecg be a sufficient bond, or does it need to be bonded to the service gec?
	
		
			
		
		
	
				
			The generator is controlled by a ats that does not open the neutral.
This is a 400-amp service and the gas meter (not bonded) is on the opposite side of the house.
Since the ats does not open the neutral, wouldn't the feeder ecg be a sufficient bond, or does it need to be bonded to the service gec?
 
				
 
 
		