Dennis Alwon said:
...plwease explain why you think this is necessary. I personally don't see why that would help.
Dennis, Trevor -
Here's my thinking: Has to do with shock hazard. The concepts come from when I was working with the amateur radio club (in hgh school - yes vacuum tubes were in common production :roll: ) - we were designing and installing transmitting antennas. The practice was to always install the ground rod at least 7 feet away from any other grounded structures. The plan was to not be able to touch both the antenna ground and another grounded structure at the same time.
Now this has carried over to when I have two metalic structures in close proximity (say within 7 feet) and one of them can be energized (such as a light pole) my inclination is to bond the two together, That way they are at the same potential and one can't get shocked by touching both.
Of course if the light pole is bonded as it should be, the risk only lasts for the milliseconds it takes the CB to trip. Now I'm starting to wonder if this is a hold over from 15 years ago, when I still clearly understood 250.4.
Have to give this some more thought.